Battery Inverter Cable Size - Tables of AWG Wire Sizes

Article Details

Last Updated
13th of April, 2020

USER OPINIONS
(51 votes)
96% thumbs up 3% thumbs down
How you rate?

Battery Inverter cable size recommendations:-

Inverter Voltage
Continuous Watts
Max. Inverter Input Amps (DC)
Fuse Size
(DC Amps)
Circuit Breaker
(DC Amps)
Wire Size (AWG)
12 Volt
600
80
80
80
2
800
107
110
110
2
1000
134
200
175
2/0
1500
200
300
250

4/0

2400
320
400
250
4/0
2500
334
400
250
4/0
2800
382
400
250
4/0
3000
400
400
250
4/0
24 Volt
600
40
50
50
8
800
54
75
75
4
1000
67
80
100
2
1500
100
110
110
2/0
2400
160
200
175
2/0
2500
167
200
175
2/0
3000
200
300
250
4/0
3500
230
300
250
4/0
4000
265
300
250
4/0
48 Volt
3000
76
110
110
2/0
3600
90
110
110
2/0
4000
148
200
175
2/0
5500
185
400
250
4/0

The larger the AWG number or wire gauge, the smaller the physical size of the wire. The smallest AWG size is 40 and the largest is 0000 (4/0). AWG general rules of thumb - for every 6 gauge decrease, the wire diameter doubles and for every 3 gauge decrease, the cross sectional area doubles.

>_The diameter information in the table applies to solid wires,
>_Stranded wires are calculated by calculating the equivalent cross sectional copper area,
>_Fusing Current (melting wire) is estimated based on 25°C ambient temperature,
>_The table below assumes DC, or AC frequencies equal to or less than 60 Hz, and does not take skin effect into account,
>_Turns of wire is an upper limit for wire with no insulation.

AWG Diameter Turns of wire
(no insulation)
Area Copper
resistance[6]
NEC copper wire
ampacity with
60/75/90 °C
insulation (A)[7]
Approximate
standard metric
equivalents
Fusing Current (copper)
(inch) (mm) (per in) (per cm) (kcmil) (mm2) (Ω/km)
(mΩ/m)
(Ω/kFT)
(mΩ/ft)
Preece
(~10s)
Onderdonk
(1s)
Onderdonk
(32ms)
0000 (4/0) 0.4600* 11.684* 2.17 0.856 212 107 0.1608 0.04901 195 / 230 / 260 3.2 kA 31 kA 173 kA
000 (3/0) 0.4096 10.405 2.44 0.961 168 85.0 0.2028 0.06180 165 / 200 / 225 2.7 kA 24.5 kA 137 kA
00 (2/0) 0.3648 9.266 2.74 1.08 133 67.4 0.2557 0.07793 145 / 175 / 195 2.3 kA 19.5 kA 109 kA
0 (1/0) 0.3249 8.251 3.08 1.21 106 53.5 0.3224 0.09827 125 / 150 / 170 1.9 kA 15.5 kA 87 kA
1 0.2893 7.348 3.46 1.36 83.7 42.4 0.4066 0.1239 110 / 130 / 150 1.6 kA 12 kA 68 kA
2 0.2576 6.544 3.88 1.53 66.4 33.6 0.5127 0.1563 95 / 115 / 130 1.3 kA 9.7 kA 54 kA
3 0.2294 5.827 4.36 1.72 52.6 26.7 0.6465 0.1970 85 / 100 / 110 196/0.4 1.1 kA 7.7 kA 43 kA
4 0.2043 5.189 4.89 1.93 41.7 21.2 0.8152 0.2485 70 / 85 / 95 946 A 6.1 kA 34 kA
5 0.1819 4.621 5.50 2.16 33.1 16.8 1.028 0.3133 126/0.4 795 A 4.8 kA 27 kA
6 0.1620 4.115 6.17 2.43 26.3 13.3 1.296 0.3951 55 / 65 / 75 668 A 3.8 kA 21 kA
7 0.1443 3.665 6.93 2.73 20.8 10.5 1.634 0.4982 80/0.4 561 A 3 kA 17 kA
8 0.1285 3.264 7.78 3.06 16.5 8.37 2.061 0.6282 40 / 50 / 55 472 A 2.4 kA 13.5 kA
9 0.1144 2.906 8.74 3.44 13.1 6.63 2.599 0.7921 84/0.3 396 A 1.9 kA 10.7 kA
10 0.1019 2.588 9.81 3.86 10.4 5.26 3.277 0.9989 30 / 35 / 40 333 A 1.5 kA 8.5 kA
11 0.0907 2.305 11.0 4.34 8.23 4.17 4.132 1.260 56/0.3 280 A 1.2 kA 6.7 kA
12 0.0808 2.053 12.4 4.87 6.53 3.31 5.211 1.588 25 / 25 / 30 235 A 955 A 5.3 kA
13 0.0720 1.828 13.9 5.47 5.18 2.62 6.571 2.003 50/0.25 198 A 758 A 4.2 kA
14 0.0641 1.628 15.6 6.14 4.11 2.08 8.286 2.525 20 / 20 / 25 64/0.2 166 A 601 A 3.3 kA
15 0.0571 1.450 17.5 6.90 3.26 1.65 10.45 3.184 30/0.25 140 A 477 A 2.7 kA
16 0.0508 1.291 19.7 7.75 2.58 1.31 13.17 4.016 — / — / 18 117 A 377 A 2.1 kA
17 0.0453 1.150 22.1 8.70 2.05 1.04 16.61 5.064 32/0.2 99 A 300 A 1.7 kA
18 0.0403 1.024 24.8 9.77 1.62 0.823 20.95 6.385 — / — / 14 24/0.2 83 A 237 A 1.3 kA
19 0.0359 0.912 27.9 11.0 1.29 0.653 26.42 8.051 70 A 189 A 1 kA
20 0.0320 0.812 31.3 12.3 1.02 0.518 33.31 10.15 16/0.2 58.5 A 149 A 834 A
21 0.0285 0.723 35.1 13.8 0.810 0.410 42.00 12.80 13/0.2 49 A 119 A 662 A
22 0.0253 0.644 39.5 15.5 0.642 0.326 52.96 16.14 7/0.25 41 A 94 A 525 A
23 0.0226 0.573 44.3 17.4 0.509 0.258 66.79 20.36 35 A 74 A 416 A
24 0.0201 0.511 49.7 19.6 0.404 0.205 84.22 25.67 1/0.5, 7/0.2, 30/0.1 29 A 59 A 330 A
25 0.0179 0.455 55.9 22.0 0.320 0.162 106.2 32.37 24 A 47 A 262 A
26 0.0159 0.405 62.7 24.7 0.254 0.129 133.9 40.81 1/0.4, 7/0.15 20 A 37 A 208 A
27 0.0142 0.361 70.4 27.7 0.202 0.102 168.9 51.47 17 A 30 A 165 A
28 0.0126 0.321 79.1 31.1 0.160 0.0810 212.9 64.90 7/0.12 14 A 23 A 131 A
29 0.0113 0.286 88.8 35.0 0.127 0.0642 268.5 81.84 12 A 19 A 104 A
30 0.0100 0.255 99.7 39.3 0.101 0.0509 338.6 103.2 1/0.25, 7/0.1 10 A 15 A 83 A
31 0.00893 0.227 112 44.1 0.0797 0.0404 426.9 130.1 9 A 12 A 65 A
32 0.00795 0.202 126 49.5 0.0632 0.0320 538.3 164.1 1/0.2, 7/0.08 7 A 9 A 52 A
33 0.00708 0.180 141 55.6 0.0501 0.0254 678.8 206.9 6 A 7 A 41 A
34 0.00630 0.160 159 62.4 0.0398 0.0201 856.0 260.9 5 A 6 A 33 A
35 0.00561 0.143 178 70.1 0.0315 0.0160 1079 329.0 4 A 5 A 26 A
36 0.00500* 0.127* 200 78.7 0.0250 0.0127 1361 414.8 4 A 4 A 20 A
37 0.00445 0.113 225 88.4 0.0198 0.0100 1716 523.1 3 A 3 A 16 A
38 0.00397 0.101 252 99.3 0.0157 0.00797 2164 659.6 3 A 2 A 13 A
39 0.00353 0.0897 283 111 0.0125 0.00632 2729 831.8 2 A 2 A 10 A
40 0.00314 0.0799 318 125 0.00989 0.00501 3441 1049 2 A 1 A 8 A

*Exact (by definition),
Conductors larger than 4/0 AWG are generally identified by the area in thousands of circular mils (kcmil), where 1 kcmil = 0.5067 mm². The next wire size larger than 4/0 has a cross section of 250 kcmil. 

Visitor Comments
No visitor comments posted. Post a comment
Post Comment for "Battery Inverter Cable Size - Tables of AWG Wire Sizes"
To post a comment for this article, simply complete the form below. Fields marked with an asterisk are required.

   Your Name:
   Email Address:
* Your Comment:

* Enter the code below:
 

Related Articles
CEB-209
Attachments
No attachments were found.
Knowledge Management by Clean Energy Brands